Shackled Designer
Member
- Location
- Decatur, AL USA
Salutations.
My present project involves planning a motion control system where the servo power supply receives 3-phase AC line power through an MCB or MMC, a contactor, and a line reactor. The contactor exists in this circuit to ensure that the servos do not move if the safety and motion control systems do not give a "ready" signal. The servo power supply is similar in some respects to a VFD, but it supplies power on a DC bus to several servo drives.
In servo/VFD power converters (or inverters) that I have used in the past, the circuit protection occurs where the feeder meets the branch (which may or may not be close to the power converter), the contactor comes usually shortly thereafter, and then the line reactor is installed in close proximity to the power converter's infeed. In the vendor's support documentation for this system, though, the device order is shown in the sample diagram as follows:
3-Phase Line --> MCB/MMC --> Line Reactor --> Contactor --> Servo Power Device
A couple questions arise out of this:
1) Is following this order likely to have significantly different operational results than reversing the positions of the contactor and line reactor?
2) If I follow the vendor's example and separate an MMC/Contactor UL508 Type E combination to put the line reactor between them, does this negate the UL combination rating?
The only change I see in 1) is where the voltage spike is directed from the reactor when the contactor opens under load {vL = -L*(di/dt)}, that is, whether the spike is absorbed by the power converter or by the line. This consideration leads me to one more question:
3) So long as I keep the line reactor close to the power converter, would it be OK to put it before the current protector and contactor, i.e. the line reactor comes between the 3-phase line and the MCB or MMC?
Is there anything else that I should consider?
Best regards,
The Shackled Designer
My present project involves planning a motion control system where the servo power supply receives 3-phase AC line power through an MCB or MMC, a contactor, and a line reactor. The contactor exists in this circuit to ensure that the servos do not move if the safety and motion control systems do not give a "ready" signal. The servo power supply is similar in some respects to a VFD, but it supplies power on a DC bus to several servo drives.
In servo/VFD power converters (or inverters) that I have used in the past, the circuit protection occurs where the feeder meets the branch (which may or may not be close to the power converter), the contactor comes usually shortly thereafter, and then the line reactor is installed in close proximity to the power converter's infeed. In the vendor's support documentation for this system, though, the device order is shown in the sample diagram as follows:
3-Phase Line --> MCB/MMC --> Line Reactor --> Contactor --> Servo Power Device
A couple questions arise out of this:
1) Is following this order likely to have significantly different operational results than reversing the positions of the contactor and line reactor?
2) If I follow the vendor's example and separate an MMC/Contactor UL508 Type E combination to put the line reactor between them, does this negate the UL combination rating?
The only change I see in 1) is where the voltage spike is directed from the reactor when the contactor opens under load {vL = -L*(di/dt)}, that is, whether the spike is absorbed by the power converter or by the line. This consideration leads me to one more question:
3) So long as I keep the line reactor close to the power converter, would it be OK to put it before the current protector and contactor, i.e. the line reactor comes between the 3-phase line and the MCB or MMC?
Is there anything else that I should consider?
Best regards,
The Shackled Designer