Order of magnitude estimate

Status
Not open for further replies.

Open Neutral

Senior Member
Location
Inside the Beltway
Occupation
Engineer
A friend hit me up with a "Hey, you're an EE, you'd know..." query. And I don't...

His employer, a non-profit, is buying a building, and there's a question as to how much service they will need; i.e. is the existing adequate to their needs.

It's 4 stories, 12,000 ft^2, and will be offices. It's a nerdy organization, so everyone has a computer; but then doesn't everyone now? [A friend in Ohio built an ISP into a 1920-30's office building. There were two 15A outlet circuits per floor when they took over the space...]

It's the Bay Area, so HVAC will be far less than in Houston or Miami.

They might add an elevator; I'd think such would go on a separate metering per PG&E.

Where do I go to start researching an estimate?
 

bob

Senior Member
Location
Alabama
Check section 220 in the NEC. Look at table 220.12 for your lighting est and receptacle load. A/C load, get a contractor to estimate the requirements. Other load
computers, office equipment, kitchen load, out door lighting, electrical heating.
Voltage? Single phase or 3 phase? None of the existing electrical equipment will be usable. Just a suggestion.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
Look around and you will find reasonable numbers based on sqft and type of use. But to really get a good idea, you need to sit down with the client and discuss how many people, what use, server room (which means A/C), and so forth.

Friends are friends, but they don't pay your rent. You might want to negotiate your fee (assuming you can legally do EE work) because this could take a little bit of effort, to do right.
 