To abide by OSHA all electrical devices must be NRTL listed. Let me say I have a UL508A listed Industrial Control Panel. The SCCR is 5kA but the available fault current is 15kA.
I decide to use supplement SB and increase the SCCR to 100kA by installing some current limiting fuses.
I know that I just lost my UL listing and even tbough I remediated a code violation in term and of 110.10, I created another one per 110.3(C).
I assume, I need a UL508A MTR and a UL Field Engineer to have my panel relabeled. Does anybody have experience with listings? OSHA can be a real trip.