Are there any arc flash label requirements other than the generic labels required by NEC 110.16? I always follow NFPA 70E, but that is not mandatory. I am in need of help on what is required for arc flash labels.
As far as I can tell, OSHA's general clause and 1910.335 require the employer to protect and alert workers to arc flash and shock hazards in the workplace, but do not require arc flash labels as discussed in NFPA 70E. They did pass a final rule for 1910.269 for arc flash and appendix E provides guidance, but it seems that it only applies to utility workers for power generation, transmission, and distribution installations.
So for the owner of a commercial building or industrial facility, if they did not want to implement arc flash labels per NFPA 70E, they wouldn't have to. They would not be required to do any more than NEC 110.16 and that is only if maintenance/servicing/examination is done on equipment while energized, right? They could, however, be fined by OSHA for non-compliance if a worker was injured because the owner did not properly assess the hazard and require the right PPE.