OSHA Standards for General Industry question

Status
Not open for further replies.

travish

Member
Location
Central North Carolina
Occupation
Electrician
2007 version of The OSHA Standards for General Industry, Section on Mechanical Power Press 1910.217(b)(8)(iv) "All a.c. control circuits and solenoid valve coils shall be powered by not more than a nominal 120volt a.c. supply obtained from a transformer with an isolated secondary"

Why would they care weather or not the xformer secondary is grounded or not? I have noticed on alot of older punch presses there is a "Grounded" light on the press to let you know if one leg is grounded,but I don't understand why they want it isolated?

thanks
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Isolated, as in a standard two winding transformer. The intent is to prohibit auto-transformers.
 