770.48 Unlisted Cables and Raceways Entering Buildings.
(A) Conductive and Nonconductive Cables. Unlisted
conductive and nonconductive outside plant optical fiber
cables shall be permitted to be installed in building spaces,
other than risers, ducts used for environmental air, plenums
used for environmental air, and other spaces used for environmental
air, where the length of the cable within the
building, measured from its point of entrance, does not
exceed 15 m (50 ft) and the cable enters the building from
the outside and is terminated in an enclosure.
(B) Nonconductive Cables in Raceway. Unlisted nonconductive
outside plant optical fiber cables shall be permitted
to enter the building from the outside and shall be permitted
to be installed in any of the following raceways:
(1) Intermediate metal conduit (IMC)
(2) Rigid metal conduit (RMC)
(3) Rigid polyvinyl chloride conduit (PVC)
(4) Electrical metallic tubing (EMT)