This might seem like a basic question but I would like some outside opinions on supporting EMT.
2002 NEC
When I run raceway I usually have the suports about 6 to 12 inches from the couplings.
Some coworkers feel that a coupling is not "other tubing terminations" and that is better to have the support in the middle of the EMT.
When it came up I read the article and I was surprised, in my mind I thought it said something about 3 ft from any fitting.
Any opinions welcome and appreciated, I would like to know if I have been doing it wrong, right or if both are OK.
[ April 29, 2003, 08:47 PM: Message edited by: iwire ]
2002 NEC
I have always treated couplings as "other tubing terminations" have I been mistaken?358.30(A) Securely Fastened. EMT shall be securely fastened in place at least every 3 m (10 ft). In addition, each EMT run between termination points shall be securely fastened within 900 mm (3 ft) of each outlet box, junction box, device box, cabinet, conduit body, or other tubing termination.
When I run raceway I usually have the suports about 6 to 12 inches from the couplings.
Some coworkers feel that a coupling is not "other tubing terminations" and that is better to have the support in the middle of the EMT.
When it came up I read the article and I was surprised, in my mind I thought it said something about 3 ft from any fitting.
Any opinions welcome and appreciated, I would like to know if I have been doing it wrong, right or if both are OK.
[ April 29, 2003, 08:47 PM: Message edited by: iwire ]