Can i use a 100 panel with 100 main breaker in the out building it is feed with a 60 amp breaker ?
Sub feed to out building running 120/240 volt 4 wires 2 hots 1 neutral 1 EGC do i connect the GLC TO THE NEUTRAL BUSS OR THE EGC BUSS?
you missed 225.33 - which contains "not more than six switches or six circuit breakers mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard or switchgear" (The "or switchgear" was added in 2014.)You need a disconnecting means. A main breaker or a switch/disconnect.
See 225.31, 225.32, and 225.36
you missed 225.33 - which contains "not more than six switches or six circuit breakers mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard or switchgear" (The "or switchgear" was added in 2014.)
If you have 6 or less branch circuits in this outbuilding a main lug panel with up to six breakers is acceptable. That is six handles not six pole spaces so one could have an 18 space main lug panel filled with all three pole breakers and still meet this section requirements.
Good point, and I may have overlooked this a time or two. May be that was never how it was intended and the reason for the change in 2014??If you are under the 2011 code or an earlier code, it is unlikely that you can use six breakers in a panel as the means of disconnect. 225.36 in the 2011 code specifies that the means of disconnect be listed as "service equipment". Almost all panelboards are listed for use as service equipment when they have a single main breaker. Those panelboards are not suitable for use as service equipment when used with more than one main breaker. This rule was changed for the 2014 code and the second building disconnect is no longer required to be listed as service equipment.
My answer to that is the guy that adds the 7th breaker is the one that created the violation.It's a wonder they don't specify a panel that will hold no more than the 6 handles. More breakers could easily be added later making the disconnect non-compliant.
I say this with a little "tongue & cheek" because of all the "what ifs" I hear from some inspectors.:happyyes:
The change in 2014 was just catching up with the change a couple of cycles ago that said you could no longer re-bond the grounded conductor at the second building. The only reason the disconnect needed to be service rated was to provide a way to bond the neutral to the GEC at the second building when that was a permitted installation method.Good point, and I may have overlooked this a time or two. May be that was never how it was intended and the reason for the change in 2014?? ...
...
I think exception 1 does allow it.The change in 2014 was just catching up with the change a couple of cycles ago that said you could no longer re-bond the grounded conductor at the second building. The only reason the disconnect needed to be service rated was to provide a way to bond the neutral to the GEC at the second building when that was a permitted installation method.
Also after additional though, I believe that 408.36 prohibits using a panelboard with multiple mains.
Actually we don't even need the exception for the second building...there should be an OCPD at the start of the feeder that would provide the required overcurrent protection of the panelboard....don't know what I was thinking when I posted that statement.I think exception 1 does allow it.
will i need a main breaker in the sub feed panel in the out building ?