Hendrix
Senior Member
- Location
- New England
Am I reading this wrong in 680,
or do they not require a disconnect in sight and 5' from edge of water?
or do they not require a disconnect in sight and 5' from edge of water?
Am I reading this wrong in 680,
or do they not require a disconnect in sight and 5' from edge of water?
Am I reading this wrong in 680,
or do they not require a disconnect in sight and 5' from edge of water?
and within sight-- no more than 50' away. :thumbsup:At least 5' from edge of water.
A disconnecting means for servicing it is required.
An emergency shut off is not required for residential hot tubs.
The problem is this. The hot tub is about 50% recessed in the deck. The disco is located underneath the deck. The EC maintains that it must be in sight of the motor, which it is being underneath the deck, but you can't see it if you are in the water.
Opinions please.
In my opinion it must be in sight of what you need to service
You don't service the water you service the pumps and other equipment.
Thank you allAgreed, the disconnect does not need to be in sight of the water but is there to service the units electrical system.