The tap conductor is wrapped to the wrong direction on the screw. Also that looks like a metal framing screw. A listed screw for this purpose would be required.
An IPC, of course. Insulation Piercing sCrew.
Also needs to be listed for Al to Cu.
Also needs to be listed for Al to Cu.
stevenje already got it: "... the undersized blue wirenut...."Looked like the violations had been covered, but found one more.
The blue wire nut is not listed for 2 #14. (or #12)
The tap conductor is wrapped to the wrong direction on the screw. Also that looks like a metal framing screw. A listed screw for this purpose would be required.
Saddle valve... that way the installer could throttle the flow of electricity as well. :roll:
I don't see arc-flash protection in place :blink: Neat and workman-like manner?
We have a winner.![]()
If the rest of the place looked like this photo, the inspector would have carpal-tunnel syndrome writing up all the violations before getting to 110.12, tho 110.12(B)(insulation damage) would be on the list somewhere.
Arc flash protection was probably via a thirty year old pair of Oakley sunglasses from a dollar store.
:bows: Thank you, I hereby would like to thank all of my plumber friends in accepting my Hack of the Month award.![]()