Out of service disconnect

I Timothy

Member
Location
Lynchburg Va.
Occupation
Faculty's Maintenance Manager
I have a 400 amp 240 volt disconnect in my office. Not in service, line conduit removed and capped off. I can't lock it out, the breaker feeding it also feeds a in use panel. can I label and lock the disconnect and then use the space in front?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
My understanding (right or wrong) is that the upstream breaker gives power to a separate panel and gives power to the switch in your disconnect. If that is right, then the safe thing to do is to have an electrician disconnect and remove the wires from the upstream breaker that feed your disconnect. Then you can have the disconnect taken away.
 

I Timothy

Member
Location
Lynchburg Va.
Occupation
Faculty's Maintenance Manager
Correction, The load side of the disconnect is removed. The disconnect is accessible. I want to use the 36" in front of it.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Correction, The load side of the disconnect is removed. The disconnect is accessible. I want to use the 36" in front of it.
If it serves no function it doesn't require working space.

110.26(A) Working Space.
Working space for equipment operating at 1000 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1), (A)(2), (A)(3), and (A)(4) or as required or permitted elsewhere in this Code.
 