I'm reviewing a report for circuit breaker testing that was performed for one of our customers. Three of the breakers had a result that was out of tolerance, and I'm looking for some input on what recommendations should be made to the customer.
Breaker #1: Square D NW30H w/ Micrologic 6.0A, 3000A
Out of tolerance parameter - ground trip time
Test result = 0.11 sec
Tolerance = 0.22 to 0.32 sec
Breaker #2: Square D MJ600 w/ Micrologic ET 1.0, 600A
Out of tolerance parameter - contact resistance
Test result: A = 82, B = 133, C = 98 (microhms)
Breaker #3: Square D JJ250 w/ TM trip unit, 250A
Test result: A = 277, B = 426, C = 345 (microhms)
So we have one breaker whose ground trip operated too quickly, and two breakers with high contact resistance values. Do you think these breakers are out of tolerance enough to warrant recommending breaker replacement? Is there any maintenance that can be performed to correct these results? Or are these results close enough to the tolerances to recommend no action at this point? I believe the breakers are only about 5 years old, so recommending replacement may not be very appealing to the customer.