larryl
Senior Member
- Location
- wrentham ma.
is a #8 bonding wire required from the disconect to the hot-tub?
larryl said:is a #8 bonding wire required from the disconect to the hot-tub?
larryl said:is a #8 bonding wire required from the disconect to the hot-tub?
the equipotential bond,,is a # 8 solid required??raider1 said:Are you talking about the equipotential bonding or the EGC for the circuit to the hot tub?
Chris
Dennis Alwon said:A #8 is not required from the disco to the Tub. I don't believe that there are too many hot tubs that need a #8 EGC so I assume you mean the bonding to the grid.
larryl said:yes, the bonding to the grid,
the EGC is a #10
larryl said:ya,sure,,
i've got a outside disconect,w/ a 20amp double pole gfi in it,,,=motor
and it also has a 30amp double pole gfi in it,,=heater
feed the disconect w/ 6-3rx,,mounted on the house
came off the disconect w/ 1" pvc,over to the tub,then to k-flex,,
ran 2-#10s=heater
ran2-#12s=motor
ran1-#10 green for the egc
hottub mounted on a concrete slab about 15 feet from the house,,
nothing else around it but a wood deck,
,,do i have to run a #8 bare c.u.,from the disconect to the tub,,to "bond" the
two of them together?
its been a couple years since i've done one,and i'm pretty sure i've done it
in the past,,
i vegly remember bonding a down spout,althougt that could of been a
*workmare
*workmare is a word i just made up,,it's when you dream your working all nite,,
thanks guys,,,,,,,