Background.
Outbuilding is fed with a single phase mwbc protected by a double pole 30A breaker
Panel in building has the following circuits
1 - 15A furnace circuit
2 - 15A lighting circuits
3 - 20A receptacle circuits
1 - 30A mwbc for air compressor.
225.39 (B) says a 60 amp disconnect, which doesn't make sense to me on a protected 30A feed.
225.39 says I can combine the ratings of the disconnects, so if I use two 30A single pole breakers and
tie the handles together (225.33(B) handle ties and 225.38(B) for Simultaneous Opening of Poles) I
meet the requirements. The part that has me confused is how can this meet the requirements, 30+30=60,
but a single double pole 30 amp breaker doesn't? Is my thinking wrong and I've missed someplace
that says that each branch of the mwbc needs a 60 amp disconnect or can you add the 30A from each branch
of the double pole breaker to get to 60A? The code says combining the ratings of all the switches or circuit
breakers for determining the rating of the disconnecting means shall be permitted. It doesn't say to differentiate
between branches it just says combine so 30+30=60.
I'm probably just overthinking this but I'd rather see the additional protection of two handle tied 30A single
pole breakers ( or a single 30 amp double pole breaker) than a 60A breaker for the disconnect or combining
the two lighting circuits to get back under the 6 hand movement rule.
Long time lurker, first time poster.
Outbuilding is fed with a single phase mwbc protected by a double pole 30A breaker
Panel in building has the following circuits
1 - 15A furnace circuit
2 - 15A lighting circuits
3 - 20A receptacle circuits
1 - 30A mwbc for air compressor.
225.39 (B) says a 60 amp disconnect, which doesn't make sense to me on a protected 30A feed.
225.39 says I can combine the ratings of the disconnects, so if I use two 30A single pole breakers and
tie the handles together (225.33(B) handle ties and 225.38(B) for Simultaneous Opening of Poles) I
meet the requirements. The part that has me confused is how can this meet the requirements, 30+30=60,
but a single double pole 30 amp breaker doesn't? Is my thinking wrong and I've missed someplace
that says that each branch of the mwbc needs a 60 amp disconnect or can you add the 30A from each branch
of the double pole breaker to get to 60A? The code says combining the ratings of all the switches or circuit
breakers for determining the rating of the disconnecting means shall be permitted. It doesn't say to differentiate
between branches it just says combine so 30+30=60.
I'm probably just overthinking this but I'd rather see the additional protection of two handle tied 30A single
pole breakers ( or a single 30 amp double pole breaker) than a 60A breaker for the disconnect or combining
the two lighting circuits to get back under the 6 hand movement rule.
Long time lurker, first time poster.