Home approximately 15 years old has a 100 amp underground feed to a remote building.
As follows is the make up of the wiring in the basement of the house:
- 1" pvc pipe from panel to a 100 amp meter socket, tap conned to the cement wall. #6 thhn copper conductors, 100 amp breaker.
(2 90 degree short radius plumbing fittings included)
- #6 has brass tubing soldered onto the wire and landed on the line side jaws of the socket.
- Meter jaws are jumpered 1/8" steel bars
- Load side wiring is 4/0 Al single conductors in 2" pvc through cement wall . Conductors in LB appear to have been put in with hammer and block of wood.
Couldn't bring myself to open the panel
️
️??
- Grounding conductor is #4 solid Cu.
Almost forgot:
Meter socket had plywood disc for cover.
Rough in inspection sticker on panel cover, no final.