I am using 12 post lights per cucuit, with 60 watt floresent bulbs. The longest run is less than 1000'.

I have used #12 and 14 NM Romex in PVC conduit (wrong type I quess), the calulation shows that with voltage and amp loss is acceptable for what i am doing.

The 2 inch PVC is above ground and will never be under water, it is attached to a 5 foot fence.

bruce
 
It would probably be cheaper for the owner to hire an Engineer to do the calculations properly, than to hire you to do it over when it doesn't work.
You did say 1000', right? One-Thousand feet?
It will not work.
db
 
This project is doomed. Type NM cable is not listed for wet locations. Exterior on a fence (even in conduit) is a wet location. What about conduit fill? You need to caculate the area of all of the cables to see if they will not exceed 40%, then you have to derate if there are more than 6 CC conductors................................................Blah Blah Blah
I don't care if it works right. but it needs to be NEC compliant and safe.
P.S. it won't work right.

Bob on the left coast.
 
thanks guys,

i have already done this on my farm and everything works great. The lights come on at dusk and turn off after a couple hours. The is no noticalbe difference between the light from the first light and the last.

I am using 2 inch PVC and 3 wires, hot, neutral and ground. I realize than NM Romex is wrong and will correct it in the future.

The volt and amp loss is minimal even at 1000' and a light every 90 feet.

So if I use #12 UF single wires for ever conductors and run two curcuits (10 bulbs on each curcuit) in the 2 inch conduit there would be no problem with this concept.

bruce
 
In your profile you state that you are a farmer.
What type of farming do you do?
How much do you plant?

To advise you on your lights, hire an electrician!
 
Please let me invite your attention to the following statement on the home page of this Forum:

This NEC? Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.

In accordance with that rule, I am closing this thread.

You are welcome to use this Forum to learn whatever you want to learn, but we cannot offer advice or assistance on performing electrical installation work at your own home. Our concern is that you may get only the answer to the question that you ask, and get no answer to the thousand other questions that you should have asked, but did not know that you needed to ask. The thousand of other questions are the ones that electricians, electrical engineers, and other professionals in the electrical industry would have known about, and would have understood the answers to, as part of their years of training.

?A little knowledge is a dangerous thing.? The Owner and Moderators of this Forum do not wish to risk allowing you and your family to be placed in danger, by giving you too little information.
 