I’m running power for a 50amp outdoor domestic cold storage container, those need disconnects correct?
If you are talking about a giant outdoor refrigerator in someone's backyard, I'm inclined to agree you would need some means to disconnect power. I don't know that the disconnecting means has to be a disconnect switch outside.I’m running power for a 50amp outdoor domestic cold storage container, those need disconnects correct?
I’m running power for a 50amp outdoor domestic cold storage container, those need disconnects correct?
Why does it need to be fused or within sight?Make sure it’s fused disconnect.
Agree with above posts. Need to be fused, and with in sight disconnect switch.
Why does it need to be fused or within sight?
??? A fuse can open, causing the motor to single phase. A breaker will open all three legs at once. But, nothing wrong with the breaker being upstream of a non-fusible disconnect.reason is safety concerns, a fuse protecting the motor is more safe for the motor than the OP
Why would the ahj care?Why wouldn’t you?
Here is why I would
reason is safety concerns, a fuse protecting the motor is more safe for the motor than the OP.
Another reason is, AHJ.
??? A fuse can open, causing the motor to single phase. A breaker will open all three legs at once. But, nothing wrong with the breaker being upstream of a non-fusible disconnect.
Motors should be protected with properly sized "overloads" or other circuit opening device based on current.
Why would the ahj care?
I'm also like others in this thread, little low on information format, in the original post.Make sure it’s fused disconnect.
Agree with above posts. Need to be fused, and with in sight disconnect switch.
It is not a code thing so the ahj has no say.AHJ cares.
portland, oregon.Where is "PDX"?
-Hal