mshields
Senior Member
- Location
- Boston, MA
I?ve got an outdoor portico that needs emergency lighting. We?d like to accomplish this with down lights in this outdoor ceiling. We do not have an emergency generator. The distance from some of the fixtures that need to be on emergency to a warm dry location for a bodine ballast is over 30 feet. So to my knowledge, this rules out bodine ballasts.
One of our lighting reps recommended going with a low voltage MR16 fixture and have that come off of a typical 12V emergency lighting battery pack (without the heads). But this, it seems to me, by itself is not going to work because these lights are going to be on under normal conditions; not just in an emergency.
OK ? so maybe we should use a power supply via which the lights would ordinarily be powered and place the battery pack in parallel with this power supply. But in this instance, it seems to me that we?ve created a low voltage DC UPS. Don?t emergency UPS?s need to be listed for that purpose?
Do you think we can do this?
Bottom line, I?m looking to put emergency down lights outside of a facility that has no generator power and for which the distant from the building to the fixtures exceeds the max distances for the application of a bodine ballast. Any suggestions?
Thanks,
One of our lighting reps recommended going with a low voltage MR16 fixture and have that come off of a typical 12V emergency lighting battery pack (without the heads). But this, it seems to me, by itself is not going to work because these lights are going to be on under normal conditions; not just in an emergency.
OK ? so maybe we should use a power supply via which the lights would ordinarily be powered and place the battery pack in parallel with this power supply. But in this instance, it seems to me that we?ve created a low voltage DC UPS. Don?t emergency UPS?s need to be listed for that purpose?
Do you think we can do this?
Bottom line, I?m looking to put emergency down lights outside of a facility that has no generator power and for which the distant from the building to the fixtures exceeds the max distances for the application of a bodine ballast. Any suggestions?
Thanks,