It is a 480V/277V, 2000A service switch located outdoors. The utility company brings the cable into the switchboard, and the switchboard is owned by the customer. According to the code, there should be no public access to the switchboard, and the metal fence should be grounded.What voltage for the service?
A few more details, is there a transformer at the service and if so who owns the transformer?
There are no requirements to ground / Bond the fence. First you need to look at where you are in the NEC: 250.194 is for over 1,000 volts. Second, note the wording that talks about exposed live parts.It is a 480V/277V, 2000A service switch located outdoors. The utility company brings the cable into the switchboard, and the switchboard is owned by the customer. According to the code, there should be no public access to the switchboard, and the metal fence should be grounded.
I would like to know the details of how to ground the fence, the ground loop, and the service ground. More detailed information would be greatly appreciated.
I understand that NEC 250.194 mentions some of this, but I would like to see a detailed drawing if possible.
Thank you in advance.