When the 2002 NEC came out, I heard a lot of fuss over the Outdoor Generator Sets (702.11 in 2005 NEC). People were saying that there had to be a disconnect on the building, outside the building, unless one could see the generator disconnecting means. To my knowledge, all manufacturers put the circuit breakers, which are the disconnecting means, in the housing.
Since the 2005 NEC, I am hearing that inside the generator enclosure is accessible and that there doesn't need to be a disconnect at the building if the generator is within 50' of the building. And in the case where the generator is more than 50', the disconnect can be inside the building where the conductors enter the building.
Is this correct? (50' is so much more definite than 'within sight').
1. If the generator enclosure is right outside the building, do I need a disconnect other than the generator CB which is inside the enclosure?
2. When I need a disconnect, may it be located inside the building where the conductors enter the building?
Since the 2005 NEC, I am hearing that inside the generator enclosure is accessible and that there doesn't need to be a disconnect at the building if the generator is within 50' of the building. And in the case where the generator is more than 50', the disconnect can be inside the building where the conductors enter the building.
Is this correct? (50' is so much more definite than 'within sight').
1. If the generator enclosure is right outside the building, do I need a disconnect other than the generator CB which is inside the enclosure?
2. When I need a disconnect, may it be located inside the building where the conductors enter the building?