Looking for some input on this;
NEC References are 2011
NEC 700.12 (B) (6) tells me when I have an outdoor gen set I do not need a disconnecting means inside the building to disconnect ungrounded conductors that serve or pass through the building. If there is a readily accessible disconnect located within site of the building.
If the gen set has a main circuit breaker for the disconnecting means which is service entrance rated (complies with 225.36 as it requires) and is within sight of the building but is located within the weatherproof enclosure which is locked does it comply with readily accessible portion of 700.12 (B) (6)?
The in the ‘explanation portion’ of the 2011 NEC handbook the definition of accessible, readily indicates it does not preclude the use of a locked door for service equipment rooms. It is a locked door however not to a room.
Any input is appreciated.
NEC References are 2011
NEC 700.12 (B) (6) tells me when I have an outdoor gen set I do not need a disconnecting means inside the building to disconnect ungrounded conductors that serve or pass through the building. If there is a readily accessible disconnect located within site of the building.
If the gen set has a main circuit breaker for the disconnecting means which is service entrance rated (complies with 225.36 as it requires) and is within sight of the building but is located within the weatherproof enclosure which is locked does it comply with readily accessible portion of 700.12 (B) (6)?
The in the ‘explanation portion’ of the 2011 NEC handbook the definition of accessible, readily indicates it does not preclude the use of a locked door for service equipment rooms. It is a locked door however not to a room.
Any input is appreciated.