I have outdoor generator set with main breaker located 50 feet away from the building it serves. The gen main breaker is not within sight of building. So right where the gen feeders enter the building their is disconnecting means call it Disco A.
The gen is separtely derived and is grounded with GEC, system bonding jumper and GES. Main breaker of Gen feeds Disco A.
The Disco A is also grounded and GEC goes to building GES.
Gen grounded I understand but Disco A grounded again is something which is weird. So when asked why Disco A is grounded again with GEC going to building GES the engineer says its per NEC 2014 Article 250.32(B)(2)(a).
Is the engineer correct or incorrect about the above?