outdoor lights

Status
Not open for further replies.
Hey guys! I want to put lamp posts around my yard,7 actually with each post able to hold 3 lamps at 100 watts max, so i guess 300 watts per posts. okay so i figuered i'd put three posts on one 15amp ckt and 4 on another because i figured 80% of the 15 amp ckt is 1440 watts. The problem is the last post will be about 360ft from the panel. I'm worried about the voltage drop. At first thought i was thinking i should run #8 or would #10 be sufficient.
 

480sparky

Senior Member
Location
Iowegia
7 posts * 3 lamps per * 100 watts per lamp = 2100 watts. 2100/120 = 17.5amps

You've already exceeded a 15-amp circuit.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You might also consider using CFL's, which would bring your total load current to below 5 amps. #12 wire would be more than plenty.
 

quogueelectric

Senior Member
Location
new york
I would just run 10 wire to the hr point of the farther ckt you should be ok on 2 ckts. The lower amperage would have less VD. Make the 3 light circuit the farther one.
 
outdoor lights

Thanks for the responses so far.One other thing i just thought of. Do these ckts need to be fed from GFI breakers? I don't think it does but just wanna make sure.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
solo618 said:
Thanks for the responses so far.One other thing i just thought of. Do these ckts need to be fed from GFI breakers? I don't think it does but just wanna make sure.
Not if you bury the wire 18" or more. I'd dig the extra 6" over suffering the GFCI headaches any day.
 

sparky59

Senior Member
the last time i had a long run for yard lights i ran a mwbc with a 2 pole 20 amp breaker. use #12 thwn and alternate the circuits....1st light black wire...2nd light red wire ...etc. You only need one neutral and there's very little voltage drop.
 

RUWired

Senior Member
Location
Pa.
With 14 awg cu., 360', 300 watts, your voltage drop will be over the recommended 3%. 12 awg will bring it up to less than 3%.10 awg will take it to 1.8%.
 

mivey

Senior Member
RUWired said:
With 14 awg cu., 360', 300 watts, your voltage drop will be over the recommended 3%. 12 awg will bring it up to less than 3%.10 awg will take it to 1.8%.
check that math again.
I get (with #10 solid):
Section, amps, Sect ft, Tot ft, Source V, Load V, Sect %VD, Tot %VD
1, 7.5, 51.4, 51.4, 120.0, 119.1, 0.77%, 0.77%
2, 7.5, 51.4, 102.9, 119.1, 118.1, 0.78%, 1.54%
3, 7.5, 51.4, 154.3, 118.1, 117.2, 0.78%, 2.31%
4, 7.5, 51.4, 205.7, 117.2, 116.3, 0.79%, 3.09%
5, 7.5, 51.4, 257.1, 116.3, 115.4, 0.8%, 3.86%
6, 5, 51.4, 308.6, 115.4, 114.8, 0.53%, 4.37%
7, 2.5, 51.4, 360.0, 114.8, 114.4, 0.27%, 4.63%
 

jdsmith

Senior Member
Location
Ohio
A lot of the GE CFL's are rated to start down to 5 degrees F or 10 degrees F. The light output will be greatly reduced since rated output is at 77 F (or maybe some other temp in the 70's). Most people I've run across don't really care about the reduced output since they get warm fuzzies about CFLs.
 