hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have outdoor menuboard sign for restaurant drive thru. The sign has power cables which has disconnect.

The menuboard sign now also has communication cable low voltage in separate conduit from power. I am wondering does the communicable need to have disconnect? I read NEC 2014 section 600.6 but their is no mention of communication cable disconnect or I don’t see one
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
It could be a fiber optic communications cable. Would that need a disconnect?
Comm cable is likely a class 2, no fire or shock hazard.
 