Does anyone know if they make an outdoor voltage disconnect for SJ cord ? I’d like to disconnect outdoor lights individually for service without a junction box on the outside. 208V
Agreed. I like the old Daniel Woodhead (Molex) watertight plugs and outlets, they have an interlocking rubber cover on both parts and a corresponding outlet cover.Maybe just a GFCI receptacle with an in-use cover, and you plug them in / out.
yeah. it's called a cord end.
SJ cord cannot be permenantly installed to replace permenant wiring - 400.12(1). as soon as you attach it to a structure, you're in violation of the NEC - 400.12(no