If the ground bar is going to be located outdoor, does it need to have an enclosure / cover?
does any manufacturer make outdoor rated ground bar?
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
Like one of these:

RACIBB-jpg-300Wx300H.jpg
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Commercial central plant, they want to install the main gear and ground bar on slab first, energy it... and build the pre-fab building to enclose them
next year.

Um, is the gear rated for outdoor use? If so, why can't the ground bus be located inside of the gear?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Commercial central plant, they want to install the main gear and ground bar on slab first, energy it... and build the pre-fab building to enclose them
next year.

You cannot use the intersystem bonding bridge in the photo in post #3.

It's a good question, I wonder if the ground bar is required to be listed for wet locations.
 