I was told by a GC that you can install NON GFI receptacles outdoors if they are at six feet or higher off the ground. Any truth to that?
See the exceptions to 210.8(A)(3) and 210.8(B)(4)I was told by a GC that you can install NON GFI receptacles outdoors if they are at six feet or higher off the ground. Any truth to that?
I have a grease collection unit that has a heat tape installed on the line. The unit is out doors and it is plugged into a gfi receptacle. the heat tape is tripping the gfi. If I install a regular receptacle with an in use cover at 6 ft. and lock the cover do you think that it is within the exceptions that the code book talks about?See the exceptions to 210.8(A)(3) and 210.8(B)(4)
Roger
I have a grease collection unit that has a heat tape installed on the line. The unit is out doors and it is plugged into a gfi receptacle. the heat tape is tripping the gfi. If I install a regular receptacle with an in use cover at 6 ft. and lock the cover do you think that it is within the exceptions that the code book talks about?
Under the 2011 you still have 426.28 and 427.22 to contend with.
Roger
I have a grease collection unit that has a heat tape installed on the line. The unit is out doors and it is plugged into a gfi receptacle. the heat tape is tripping the gfi. If I install a regular receptacle with an in use cover at 6 ft. and lock the cover do you think that it is within the exceptions that the code book talks about?
Am I correct, that these sections reference ground-fault protection (GFP) as opposed to GFCI protection ?
If so, could the heat tape be hard-wired to a GFP protected circuit ?
Taking into account removing the plug would be altering the tape, if that were acceptable by the AHJ, could that be a solution (hard-wiredd to a GFP circuit or allowing the tape to be converted to a twist lok)
(A Breaker such as Square-D QPGFEP1015 would provide this)