N nizak Senior Member Jun 24, 2024 #1 When the code says “ self contained” this is in regards to a hot tub. Possibly a factory assembled unit with pumps, blowers, and heaters all inclusive? Not a site built concrete or gunnite type. Thanks
When the code says “ self contained” this is in regards to a hot tub. Possibly a factory assembled unit with pumps, blowers, and heaters all inclusive? Not a site built concrete or gunnite type. Thanks
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jun 24, 2024 #2 nizak said: When the code says “ self contained” this is in regards to a hot tub. Possibly a factory assembled unit with pumps, blowers, and heaters all inclusive? Not a site built concrete or gunnite type. Thanks Click to expand... Yes, that is correct
nizak said: When the code says “ self contained” this is in regards to a hot tub. Possibly a factory assembled unit with pumps, blowers, and heaters all inclusive? Not a site built concrete or gunnite type. Thanks Click to expand... Yes, that is correct
N nizak Senior Member Jun 24, 2024 #3 Dennis Alwon said: Yes, that is correct Click to expand... Would perimeter bonding of the concrete slab it sits on be required?
Dennis Alwon said: Yes, that is correct Click to expand... Would perimeter bonding of the concrete slab it sits on be required?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jun 24, 2024 #4 nizak said: Would perimeter bonding of the concrete slab it sits on be required? Click to expand... The bonding of perimeter surfaces per 680.26(B)2) is required unless all of the conditions in 680.42(B) are met.
nizak said: Would perimeter bonding of the concrete slab it sits on be required? Click to expand... The bonding of perimeter surfaces per 680.26(B)2) is required unless all of the conditions in 680.42(B) are met.