Hi guys,
Installing a exterior subpanel on a dwelling unit. The sub panel will hold a 50 amp breaker for a 10.5kw sauna and a 15 amp breaker for two LED lights and one general use receptacle.
Gonna run 3/4inch EMT with #6 THWN conductors (2 hots, 1 grounded conductor, 1 #10 grounding conductor) 60 amp breaker inside for the subpanel.
My calculated load is 43.75 amps for the sauna. Am I OK adding the one 15 amp circuit for general lighting.
Thanks in advance for any info on this setup.