Outdoor Sauna panel load calculation

Tutone

Member
Location
Minnesota
Occupation
Master Electrician
Hi guys,
Installing a exterior subpanel on a dwelling unit. The sub panel will hold a 50 amp breaker for a 10.5kw sauna and a 15 amp breaker for two LED lights and one general use receptacle.
Gonna run 3/4inch EMT with #6 THWN conductors (2 hots, 1 grounded conductor, 1 #10 grounding conductor) 60 amp breaker inside for the subpanel.
My calculated load is 43.75 amps for the sauna. Am I OK adding the one 15 amp circuit for general lighting.
Thanks in advance for any info on this setup.
 
My calculated load is 43.75 amps for the sauna. Am I OK adding the one 15 amp circuit for general lighting
Given the loads I don't see an issue with adding the 15 amp branch circuit to the feeder calculation with a 60 amp feeder.
 
Given the loads I don't see an issue with adding the 15 amp branch circuit to the feeder calculation with a 60 amp feeder.
Thanks Infinity. Figured I was OK. It would get pretty spendy if I had to go to a 70 amp feeder for this.
 