I have undertaken the installation of a portable spa outdoors on a deck connected to my house.
The disconnect box that I bought has a removable link, not a breaker, then a GFCI, then an additional 15 Amp breaker for an outdoor outlet to be installed <10 ft, and > 20 ft from the tub.
My plan was to attach the dicsonnect box about 8 feet from the hot tub, within code provisions. I am running 6/3 AWG to a box in the attic, and splicing to 6 AWG THWN wire inside EMT from the attic to the disconnect.
From the disconnect I ran 1/2 in EMT to the required outdoor outlet, all connected to the house, and under the deck, not contacting the ground. Then, ran 3/4 in EMT to the spa, again attached to the house, and then through the beams of the deck, not toughing ground.
Questions are,
1) Is the NM cable from service to the disconnect allowable, as I can't tell from the discussions whether the circuit is a feeder or branch.
2) Is the splice in the box in the attic OK?
3) Is EMT allowable for outdoor use with compression connectors if attached to the house, or deck without touching the ground.
Thanks in advance for your comments.
Bryan
Questions are,