Outdoor spa tripping GFCI
James L
Kansas Cty, Mo, USA
I did a panel change out last summer, and one of the breakers was for an outdoor spa
There's an old spa panel outside and it has about (4) breakers in it, none GFCI
I told him the least expensive option would be a 50 amp GFCI 2-pole in the panel inside, so that's the route he went
He just called me couple of days ago and said that 50 amp breaker keeps tripping everyday, whereas it had never tripped before.
That's easy enough, except for one wrinkle...
He said it only trips at night. He said he has waited there as late as 10:30 p.m. with everything running and it never trips. So he'll go home and come back in the morning to find that it's tripped.
I know it's very limited info, but does anything stand out?
I've never had good luck with a GFCI breaker feeding anything outside if the load is very far away. You get cumulative leakage that adds up to above the threshold of the GFCI and trips it. I would opt to put the GFCI outside at the load. You can buy a spa disconnect with a 50A GFCI breaker in it cheaper than buying just a GFCI.
I suggested that, except the heater can't be on without the pump
But the pump can be on without the heater. Night one pump on, heater off, if GFCI holds the problem is not the pump circuit.
The odds are it is a problem with the heater. Is there a high heat mode that turns on when it gets cold later at night?
The high heat mode is a good question.