Comiskeyelectric
Member
- Location
- Texas
- Occupation
- Electrical contractor
Need some help!! We recently wired a outdoor stage for music venues. Pretty simple installation with 6 - 20A 120v circuits. We GFCI protected all outlets. Well now they have had a few concerts and we have a problem with the GFCI’s randomly tripping. I believe this isnt due to faulty equipment but to current leakage from the band’s equipment. Reading through the code book 520.9 states “ A branch circuit of any size supplying one or more receptacles shall be permitted to supply stage set lighting. The voltage rating of the receptacles shall be not less than the circuit voltage. Receptacle ampere ratings and branch circuit conductor ampacity shall not be less that the branch circuit overcurrent device ampere rating. Table 210.21(B)(2) and 210.23 shall not apply. The application of 210.8(B)(4) shall not be required.” With this code would it be permissible to remove the GFCI protection being that these are dedicated for stage equipment and not accessible by the public. Thank you.