Got a customer with an outdoor subpanel that feeds outdoor landscape loads and his dock on a lake. The electrical inspector says the entire sub panel must be GFI protected. Problem is that the soil conductivity is extremely high and even though the utility meter base where the neutral and earth ground are bonded together is over 120 ft away, there is still continuity between neutral ground all the way down at the outdoor sub panel. With all the wires in the conduit (2 Hots, a neutral and a ground) unhooked and isolated from each other there's no path to ground. But when the neutral up at the meter base gets landed on the neutral bus inside the meter base there is now continuity at the outdoor sub panel from the neutral to the ground rod at the sub panel. There is a separate breaker inside the meter-base that feeds power down to the outdoor sub-panel. 60 amp GFCI breaker that's inside the outdoor subpanel won't function properly, due to the neutral-earth ground short. Breakers are Eaton CH series. Is there anyway to isolate this sub-panel to make a GFCI work? The neutral bar inside the sub-panel is on plastic risers and does not connect to the ground bar. With the main #4 solid copper ground wire removed from the meter-base, there is still continuity from the meter-base Neutral buss bar and ground wire. PoCo came out and spent 2 hours to tell me "Guess its just really conductive dirt". 400 amp underground power feed.
Is there technology or a different method to get a 2 pole GFCI to work here? Or am I overlooking something?