I want to get thoughts on where to connect the GEC if both the source (outdoor transformer) and first disconnecting means/service are located within a common ground grid.
For separately derived systems with an outdoor transformer, the SBJ and GEC would be connected only at the source and you would be compliant with 250.30(C).
But for a service supplied system, how can you be code compliant to have your MBJ and GEC in your service entrance and an additional GEC connection at the outdoor transformer? Wouldn't objectionable current be present because of the common ground grid?
For separately derived systems with an outdoor transformer, the SBJ and GEC would be connected only at the source and you would be compliant with 250.30(C).
But for a service supplied system, how can you be code compliant to have your MBJ and GEC in your service entrance and an additional GEC connection at the outdoor transformer? Wouldn't objectionable current be present because of the common ground grid?