outdoor transformer oil containment NEC and 450.23

Status
Not open for further replies.

Chunkie

Member
Location
calgary
Occupation
electrical designer
I'm trying to define the containment requirements for an oil filled transformer what exaclty is the code requirements for containment for an oil filled transformer. i've read 450.23 and it refers to fm global ,and there the confusion starts. any help appreaciate, please refernce code for understanding requirements. cheers.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
This is not an NEC issue. You will need to go to other standards, primarily those associated with fire prevention, such as the old Factory Mutual, now FM Global.
 

mnelson

Member
Location
Tomah, WI
Occupation
Eng Tech
I'm trying to define the containment requirements for an oil filled transformer what exaclty is the code requirements for containment for an oil filled transformer. i've read 450.23 and it refers to fm global ,and there the confusion starts. any help appreaciate, please refernce code for understanding requirements. cheers.
You may want to look NFPA 850 or 70 depending on your situation.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The last time I was involved with containment, we needed to check with the Dept of Natural Resources as we had a waterway near by.
 