Today I was on a roof removing some old satellite dishes and an old TV antenna which is being replaced.  I noticed that the old antenna and none of the three dishes were grounded (do any of these dish companies follow the NEC).  With the dishes gone and only a new antenna in place the proposed fix for the problem is for the TV antenna mast to have a #10 grounding conductor run as short as possible and straight down to an 8' ground rod.  From that rod there a #6 bonding jumper will run to the single rod current installed for the service.  There is no existing intersystem bonding termination so that requirement is not a factor.  Also connected to the new rod will be an antenna discharge unit with a separate #10 to the rod.  Anyone see any code issues?
	
		
			
		
		
	
				
			 
				
 
 
		