Outdoor Wood Stove

Merry Christmas

frofro19

Senior Member
Location
VA.
Occupation
Master Electrician
I have a customer that has a Hardie outdoor wood stove that's having trouble with the GFCI tripping. The stove is approximately 13 years old and once you remove the back cover, there's a GFCI receptacle that the pump and the fan is plugged into. Sometimes if the fan appears to not be working correctly, there's some moisture in there and the GFCI trips. Does this stove have to have the GFCI receptacle or could the pump and fan wire be direct wired into the junction box inside the stove where the current GFCI receptacle is and eliminate the GFCI receptacle?
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Is this thing listed, as a whole assembly?

Wouldn't think it would need GFCI protection. The fact they used a receptacle complicates things a little, yet if inside the unit still don't think it would require GFCI protection. Maybe they afraid someone will use same receptacle to plug other items into - when in reality there maybe should be a receptacle located outside the unit for servicing purposes?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
With a unit that old sitting outside there will be leakage current. interesting it has internal GFCI. Might have been to avoid a cord end GFCI. I would dry out the wiring and replace GFCI with a WR type. The WR types have coated circuit boards, that may solve the tripping
 