tl;dr - How would you tackle the installation of an outlet above a fireplace?
I've been a lurker for years and have usually found the answer to my question(s) just by searching, but I'm coming up just a little short this time around and could use some help. I am not an electrician, but was a contractor for many years.
I hired a contractor to install a new fireplace (gas fired unit) in my home. After 3 days, I fired them because their work was atrocious. Nothing square, plumb or level and they missed several critical heat clearances that were clearly defined in the install docs. I've torn out everything they did and rebuilt it properly and am almost ready for mechanical inspection.
The design calls for a TV to be hung on the wall above the fireplace and as such, I need to get an outlet up into that area. (see attached pics)
The previous installation had outlets in the face of the hearth and I removed those and pulled the wire back, ran it up the wall and poked it through the king and trimmers where you can see it at the right side of the popout opening. I'd like to place the outlet about 16" to the left of where the wire comes through the framing, but I'm concerned about heat generated by the fireplace once this is all closed off.
I initially contacted a local electrical firm who normally does large commercial jobs to see if they would help me figure this out or, just come out and do the work (I know time is valuable). I sent them pics and had a couple phone calls with them and they've gone dark. No contact for over a week so I assume they're not interested.
I popped in here to start reading and found several threads and some good info on where to look for a solution:
Between those threads and reading the NEC, I *think* I have a basic path forward, but I'm having a tough time just sourcing the Type-Z wire. I've reached out to several wire manufacturers, (Southwire, Allied, etc) and they've all basically told me they can't help me and to try my local home improvement store or online electrical supply houses. Of course, Home Depot etc doesn't carry anything high-temp and the online outfits all want me to buy 100+ foot spools. Where can one find a 25' coil of this stuff?
I have wire on hand (14 AWG, Silicone, 7 strand tinned copper, 200C rating stamped on the jacket) but it doesn't meet NECs marking provisions so I'm hesitant to use it. Assuming I can find a short piece of Type-Z, I'm looking at the black Gardner Bender hi-temp wire nuts (GB-4s?) and high-temp crimp on terminals and am planning on using a metal J-box and either EMT or flexible conduit. Not sure which way to go with the outlet itself though as I haven't found any temp ratings for the units I have on hand - I'm not averse to buying a different outlet. The only load on this circuit will be the fireplace itself, the TV, a cable box, a Bluray player and *maybe* a soundbar. Looks like a tick over 7A total based on the labels on the gear.
The framing above the fireplace will all be steel stud and insulated with 3.5" mineral wool batts and I was going to 'sandwich' the conduit and box with those batts.
There *are* two 3" outside air ducts entering this space and I *may* put small fans (110V@20W) on them to force air in, but currently it's set up for convection only.
Am I on the right path or do I need to keep reading?
Thx!
I've been a lurker for years and have usually found the answer to my question(s) just by searching, but I'm coming up just a little short this time around and could use some help. I am not an electrician, but was a contractor for many years.
I hired a contractor to install a new fireplace (gas fired unit) in my home. After 3 days, I fired them because their work was atrocious. Nothing square, plumb or level and they missed several critical heat clearances that were clearly defined in the install docs. I've torn out everything they did and rebuilt it properly and am almost ready for mechanical inspection.
The design calls for a TV to be hung on the wall above the fireplace and as such, I need to get an outlet up into that area. (see attached pics)
The previous installation had outlets in the face of the hearth and I removed those and pulled the wire back, ran it up the wall and poked it through the king and trimmers where you can see it at the right side of the popout opening. I'd like to place the outlet about 16" to the left of where the wire comes through the framing, but I'm concerned about heat generated by the fireplace once this is all closed off.
I initially contacted a local electrical firm who normally does large commercial jobs to see if they would help me figure this out or, just come out and do the work (I know time is valuable). I sent them pics and had a couple phone calls with them and they've gone dark. No contact for over a week so I assume they're not interested.
I popped in here to start reading and found several threads and some good info on where to look for a solution:
higher temp wires and termintion rules
On higher temp cables for example #14 Type Z rated at 150c the value in 310.15(B)18 is 34amps. In what condition can I use it at full ampacity? In 110.14(C)(1) it speaks of the terminations limiting the cable use? So I imagine there is no 150c Connectors? So other than for ambient temp...
forums.mikeholt.com
Type Z Conductors
I have a few generator jacket heaters that require a minimum of 125° C conductors in the heater junction box. The supplier has type Z, 150° C insulation, how would you size the conductors for a 4000W, 208 volt, 1Ø heater? From the panel to another junction box there will #10 THHN fed from a 30...
forums.mikeholt.com
Understanding 110.14(C) - Temperature Limitations
I have a lot of trouble understanding NEC 110.14(C) because I don't really understand where the heat comes from and what we are trying to protect from what. Are we worried about (1) the heat generated in the conductor, (2) the heat generated by the equipment at it's terminals, or (3) the ambient...
forums.mikeholt.com
High-Temp Building Wire?
I was reading a manual for a commercial kitchen ventilation hood and came across this warning: All field wiring on top of the hood must use high temp wire and wire nuts (black). Wiring must be routed through hard or flex conduit. Route and attach all conduit on top of, or above, structural...
forums.mikeholt.com
Between those threads and reading the NEC, I *think* I have a basic path forward, but I'm having a tough time just sourcing the Type-Z wire. I've reached out to several wire manufacturers, (Southwire, Allied, etc) and they've all basically told me they can't help me and to try my local home improvement store or online electrical supply houses. Of course, Home Depot etc doesn't carry anything high-temp and the online outfits all want me to buy 100+ foot spools. Where can one find a 25' coil of this stuff?
I have wire on hand (14 AWG, Silicone, 7 strand tinned copper, 200C rating stamped on the jacket) but it doesn't meet NECs marking provisions so I'm hesitant to use it. Assuming I can find a short piece of Type-Z, I'm looking at the black Gardner Bender hi-temp wire nuts (GB-4s?) and high-temp crimp on terminals and am planning on using a metal J-box and either EMT or flexible conduit. Not sure which way to go with the outlet itself though as I haven't found any temp ratings for the units I have on hand - I'm not averse to buying a different outlet. The only load on this circuit will be the fireplace itself, the TV, a cable box, a Bluray player and *maybe* a soundbar. Looks like a tick over 7A total based on the labels on the gear.
The framing above the fireplace will all be steel stud and insulated with 3.5" mineral wool batts and I was going to 'sandwich' the conduit and box with those batts.
There *are* two 3" outside air ducts entering this space and I *may* put small fans (110V@20W) on them to force air in, but currently it's set up for convection only.
Am I on the right path or do I need to keep reading?
Thx!