Here's why...
Here's why...
Since the grounded current carrying conductor (neutral) at the outlet will be carrying current and it has a measurable amount of resistance / impedance, that means that there will be a voltage drop across that length of conductor. If there is a voltage drop, that means there is a measureable voltage difference at the white wire at the outlet when compared to another ground path, such as metal piping, damp concrete and such. Therefore, a person coming in contact with the neutral and a (different) ground path would feel that voltage drop. If the current were to increase dramatically, albeit for a very short period of time, due to a short within a powertool for example, the voltage drop would also rise, presenting an even greater potential difference to the person holding the tool (if well grounded himself). THAT is one very imporatnt reason for a separate EGC and why sub-panels need to have isolated neutrals. The neutral and ground must anly be connected at one locattion only and that must be at the source. We must remeber that current does not take only the path of least resistance, but takes all paths in different proportions according to Ohm's law.