Outlet installed at 240V instead of 120 and no ground?

Status
Not open for further replies.

ee_trojan

Member
Location
Los Angeles, CA
I moved into a newly renovated apartment on the first and the air conditioner was not working. After testing the receptacle with a multimeter it is 240V and there is no ground installed, and the AC unit requires 115V. After discovering this I tested some other receptacles and about half don't have a ground wire.

Are grounds required at every receptacle by code?

Is it dangerous for this outlet to have 240V across it?

What is the best way to go about getting this fixed?

Also, for my own curiosity would renovation of a single apartment unit require a PE to be involved? Or is this something a contractor can just come in and do on their own?

IMG_0375.jpg
 
What is the wiring method used to feed the receptacle? It could be that the metal boxes are grounded and the device is self-grounding. The 240 volts across a 120 volt receptacle is a different story.

Welcome to the Forum. :)
 
That type of NEMA configuration is listed to go with 120 volts. 240 volts would be a hazard if someone plugged in a 120 volt device which is probably a given considering no one would think twice. I would not either.
 
Yes, this outlet was specifically for an air conditioning unit 115V which I believe was damaged by the higher voltage. Not my AC unit but still not good.

How should I go about getting this fixed? I know some electrical engineering but this is not my unit, I just moved in.
 
Yes, this outlet was specifically for an air conditioning unit 115V which I believe was damaged by the higher voltage. Not my AC unit but still not good.

How should I go about getting this fixed? I know some electrical engineering but this is not my unit, I just moved in.

Any competent licensed electrical contractor should be able to address this problem. PE or EE not required.
 
I moved into a newly renovated apartment on the first and the air conditioner was not working. After testing the receptacle with a multimeter it is 240V and there is no ground installed, and the AC unit requires 115V. After discovering this I tested some other receptacles and about half don't have a ground wire.

Are grounds required at every receptacle by code?

Is it dangerous for this outlet to have 240V across it?

What is the best way to go about getting this fixed?

Also, for my own curiosity would renovation of a single apartment unit require a PE to be involved?


#1- Like infinity implied, the egc may not be visible if the wiring method is conduit/ AC cable, etc. As for the pic, there could have been a former 6-15 (240v) receptacle for an AC unit, and somebody got a 240 window ac with a jury rigged 120v (5-15) cord cap and changed the receptacle to accommodate it- yes, that has happened.

#2- Yes- devices that accept 120v plugs cannot have 240 accross the device. Someone could smoke something by plugging 120v equipment into this receptacle.

#3 Contact a licensed reputable EC

#4 NO. If you do #3, they will know what to do.:D
 
Last edited:
Yes, this outlet was specifically for an air conditioning unit 115V which I believe was damaged by the higher voltage. Not my AC unit but still not good.

How should I go about getting this fixed? I know some electrical engineering but this is not my unit, I just moved in.

If you are renting, call the landlord. This should be a free fix. This is not something you should be doing given your skill set and that in many areas having tenants doing electrical is a liability.
 
If you are renting, call the landlord. This should be a free fix. This is not something you should be doing given your skill set and that in many areas having tenants doing electrical is a liability.
Copy that! Also, check with your building dept. to see if they have a rental inspection program. (My town does).
Good luck
 
I moved into a newly renovated apartment on the first and the air conditioner was not working. After testing the receptacle with a multimeter it is 240V and there is no ground installed, and the AC unit requires 115V. After discovering this I tested some other receptacles and about half don't have a ground wire.

Are grounds required at every receptacle by code?

Is it dangerous for this outlet to have 240V across it?

What is the best way to go about getting this fixed?

Also, for my own curiosity would renovation of a single apartment unit require a PE to be involved? Or is this something a contractor can just come in and do on their own?

View attachment 18155
You may want to verify that the receptacle with 240V present, isn't part of a multi wire branch circuit in which the grounded conductor has been compromised. Losing a neutral in a multi circuit, branch circuit will apply 240V to downstream equipment.
 
I moved into a newly renovated apartment on the first and the air conditioner was not working. After testing the receptacle with a multimeter it is 240V and there is no ground installed, and the AC unit requires 115V. After discovering this I tested some other receptacles and about half don't have a ground wire.

Are grounds required at every receptacle by code?

Is it dangerous for this outlet to have 240V across it?

What is the best way to go about getting this fixed?

Also, for my own curiosity would renovation of a single apartment unit require a PE to be involved? Or is this something a contractor can just come in and do on their own?

View attachment 18155

Where were you measuring 240 volts?
If you were measuring it in the slots that are on top of each other, (as shown in your pic) that would be bad. If measuring in slots beside each other, it could possibly be a split receptacle.
 
Welcome to the forum. As others wrote, this is a problem for the landlord, not you. However, if that weren't the case, or you just want to know what is going on, and to answer your questions:

Where were you measuring 240 volts?
If you were measuring it in the slots that are on top of each other, (as shown in your pic) that would be bad. If measuring in slots beside each other, it could possibly be a split receptacle.

Good point. However, the OP should have 120V and 120V only between:

1) Either "hot" to ground
2) Either "hot" to "neutral"

A split receptacle with 240V would only show up if measuring voltage hot to hot and two different legs were used, otherwise the voltage between the two hots would be zero.

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~


I moved into a newly renovated apartment on the first and the air conditioner was not working. After testing the receptacle with a multimeter it is 240V and there is no ground installed, and the AC unit requires 115V. After discovering this I tested some other receptacles and about half don't have a ground wire.

Are grounds required at every receptacle by code?

Is it dangerous for this outlet to have 240V across it?

What is the best way to go about getting this fixed?

Also, for my own curiosity would renovation of a single apartment unit require a PE to be involved? Or is this something a contractor can just come in and do on their own?

View attachment 18155

1) All 3 prong 120V receptacles are now (and for some time) require to be grounded or have GFCI protection, either thru being a GFCI receptacle, being on the load side of a GFCI receptacle, or on a circuit protected by a GFCI breaker.

2) Yes, very. That is a NEMA 5-15 receptacle made for 3 wires: one hot @ 120V (small slotted hole, can be any color of wire except green or white), one neutral (longer slotted hole, must be a whte wire) and a ground/EGC (round hole, will either be green or bare). Since all 120V appliances use that plug, anything plugged into that receptacle with an unmodified factory plug, save for something like a computer tower with a 120/240V selector switch set on 240V, will probably blow up instantly or nearly so.

3) Aside from having the landlord fix it, a licensed electrician.

Do you have any pictures with the receptacles removed?

Chances are they used to/were planning on having 240V for the AC units and now have 120V. This would require changing the receptacle from a NEMA 6-15 or 6-20 to a 5-15 or 5-20, removing one of the ungrounded conductors (white wire would be easiest/more correct) from a 2p breaker and landing it on the neutral buss (or on the neutral spot on a 1p AFCI/GFCI breaker), changing the 2p breaker out for a single pole, and ensuring the neutral has been re-identified (easiest if the white was used a hot when wired to 240V).

If the box is metal and it is AC cable or metal conduit back to the panel, a self-grounding receptacle is sufficient to complete a ground path to the appliance. I'd still prefer to pigtail to the box should the receptacle ever get loose or a replacement of the non-grounding type be used. A GFCI receptacle would be better still.

If the box is plastic or a NM type wire is feeding it, and there is only 2 wires per cable, you cannot ground the outlet w/o running new wire. In those cases, a GFCI receptacle is mandatory.
 
The receptacle and plate look new compared to the wall. I wonder if a combination 125/250 volt receptacle was replaced with a 125 volt receptacle and mis-wired? This was a common installation in apartments so that the renter could use either a 120 volt or a 240 volt air conditioner.
 