I can't find the code that states I must install a receptacle on the pole when installing an outside main breaker box. Inspector just failed me for this. Can anyone please tell me the code that covers this please
I can't find the code that states I must install a receptacle on the pole when installing an outside main breaker box. Inspector just failed me for this. Can anyone please tell me the code that covers this please
I can't find the code that states I must install a receptacle on the pole when installing an outside main breaker box. Inspector just failed me for this. Can anyone please tell me the code that covers this please
I can't find the code that states I must install a receptacle on the pole when installing an outside main breaker box. Inspector just failed me for this. Can anyone please tell me the code that covers this please
Not a temporary service. This pole is for a pole barn we just haven't ran the wire to the barn yet. It's on the water so we had problems with getting the permits to begin with so it's considered just service. The pope is 100' from the house. Just called inspector and waiting for his call back with the code he is referencing
I can't find the code that states I must install a receptacle on the pole when installing an outside main breaker box. Inspector just failed me for this. Can anyone please tell me the code that covers this please
Not a temporary service. This pole is for a pole barn we just haven't ran the wire to the barn yet. It's on the water so we had problems with getting the permits to begin with so it's considered just service. The pope is 100' from the house. Just called inspector and waiting for his call back with the code he is referencing
Even if the Pope WAS within 100 feet of the house, I doubt that He is still there ! Usually at the Vatican I believe.
210.64, 2017 code:210.64 Electrical Service Areas
At least one 125-volt, single-phase, 15- or 20-ampere-rated receptacle outlet shall be installed within 15 m (50 ft) of the electrical service equipment.
Exception: The receptacle outlet shall not be required to be installed in one-and two-family dwellings.
210.64 Electrical Service Areas.
At least one 125-volt, single-phase, 15- or 20-ampere-rated receptacle outlet shall be installed in an accessible location within 7.5 m (25 ft) of the indoor
electrical service equipment. The required receptacle outlet shall be located within the same room or area as the service equipment.
Exception No. 1: The receptacle outlet shall not be required to be installed in one- and two-family dwellings.
Exception No. 2: Where the service voltage is greater than 120 volts to ground, a receptacle outlet shall not be required for services dedicated to equipment covered in Articles 675 and 682
inspector stated that although this is just a panel install for the pole barn and the wire just needs to be ran to the barn (customer is doing as they can afford) he needed a plug to test it for the final inspection.
It is lame but I would add an outlet to the one side of the panel... because if nothing else it gives me a power spot for tools there... maybe a set up for an rv that has the power split between 30 and 20 amp lugs... gives one a load of opportunities near the barn that way.
But, not the farmer so..just know that we did it that way on the farm I worked at One summer near Smiths Mountain Lake...