outlets above base-board heaters
Re: outlets above base-board heaters
See 210.52
Permanently installed electric baseboard heaters equipped with factory-installed receptacle outlets or outlets provided as a separate assembly by the manufacturer shall be permitted as the required outlet or outlets for the wall space utilized by such permanently installed heaters. Such receptacle outlets shall not be connected to the heater circuits.
FPN: Listed baseboard heaters include instructions that may not permit their installation below receptacle outlets.
The fpn says that in some cases baseboard heaters may not be installed below electric receptacles. It would depend on the watts per running ft of the baseboard. If the baseboard is low density (177 watts) yes you can. If it is 210 watts per running foot, no you can't