Outlets on roof of Industrial Building

Status
Not open for further replies.

dasarmin

Member
Location
Texas
A few years ago on a new warehouse construction, exhaust fans were installed on the roof. Along with the Exhaust Fans, water proof Outlets were required. This requirement I believe came from the MEP who provided the drawings. I seem to remember when I ask about these outlets, that these were a requirement from NEC. In what section would this be addressed?
 
I don't believe the NEC requires receptacles for a fan but they are required for a/c units. If they are on the roof then gfci is required per 210.8(B)

Art. 210.63 requires a receptacle for heating a/c and refrigeration. If the fan is considered a cooling system them it could be req. by this article
 
I don't believe the NEC requires receptacles for a fan but they are required for a/c units. If they are on the roof then gfci is required per 210.8(B)

Art. 210.63 requires a receptacle for heating a/c and refrigeration. If the fan is considered a cooling system them it could be req. by this article

I agree, it is very common for a unit containing refrigerant to need a receptacle to run a portable pump for most any service work involving removing or replacing refrigerant. A unit that is just a fan will not have as much need for such accessory devices during servicing.
 
anyone trying to work on these things in the future will appreciate having power up there. I don't think it is code required but it is certainly something that is useful.

I have occasionally wondered why the code does not require outlets on roofs where there is electrical equipment that will need servicing.
 
anyone trying to work on these things in the future will appreciate having power up there. I don't think it is code required but it is certainly something that is useful.

I have occasionally wondered why the code does not require outlets on roofs where there is electrical equipment that will need servicing.

I agree it would be a good idea and probably should be required. I bet on most plans there will be a receptacle called for if there is equipment up there. With all the portable equipment (battery powered) the demand is not as great.
 
anyone trying to work on these things in the future will appreciate having power up there. I don't think it is code required but it is certainly something that is useful.

I have occasionally wondered why the code does not require outlets on roofs where there is electrical equipment that will need servicing.

You are much more likely to need power to service a refrigerant compressor unit than a blower only unit. I believe the NEC recognizes the fact that refrigerant recovery units and vacuum pumps are very common to that trade and if there is a unit installed with refrigerant, a receptacle for those purposes will be used at some point on virtually all installations.

Even if there is no electric powered equipment on a roof doesn't mean someone will not use power on the roof at some time, do you think there should be at least one receptacle on every roof?
 
You are much more likely to need power to service a refrigerant compressor unit than a blower only unit. I believe the NEC recognizes the fact that refrigerant recovery units and vacuum pumps are very common to that trade and if there is a unit installed with refrigerant, a receptacle for those purposes will be used at some point on virtually all installations.

Even if there is no electric powered equipment on a roof doesn't mean someone will not use power on the roof at some time, do you think there should be at least one receptacle on every roof?

I think the typical single family residence would not benefit enough to make it worth mandating.

For installations that have equipment that might need servicing located on a roof, it will be very handy eventually.

If you have to go out on a roof at night and work by flashlight, you will greatly appreciate an outlet to plug in a work light.

I am not sure why the need to power a small compressor that could be powered from an extension cord requires an outlet. It is just a convenience, and not an electrical safety issue.
 
I think the typical single family residence would not benefit enough to make it worth mandating.

For installations that have equipment that might need servicing located on a roof, it will be very handy eventually.

If you have to go out on a roof at night and work by flashlight, you will greatly appreciate an outlet to plug in a work light.

I am not sure why the need to power a small compressor that could be powered from an extension cord requires an outlet. It is just a convenience, and not an electrical safety issue.

Actually another requirement kicks in for AC equipment that likely puts a receptacle on the roof in a lot of cases anyway - the receptacle that is needed within 25 feet of the equipment.
 