boboelectric said:
Reread the question. answer, No.
Bob O. 84,Pa.15330

Bob, what article do you think prohibits it?

Roger
 
Are you saying "no" to the OP or that the FAQ is not addressing the question?

Roger
 
boboelectric said:
No?

Bob O>84,Pa.15330

No what?

There is nothing prohibiting a 20 amp single receptacle from being installed on a 15 amp circuit.

Roger
 
I agree with Bob.

If you plug a 20A appliance it will overload the circuit, no?

15A duplex on a 20A is Ok not vice versa.

Tom
 
boboelectric said:
Sorry. What I read was "can I put a single 20 Amp receptacle on a 15 amp circuit?"
No.
Bob O.84,Pa.15330

And you can, so the answer would be yes.

Roger
 
Let's look at 210.21(B)(1) as pointed out by Dennis in post #2.

(B) Receptacles
(1) Single Receptacle on an Individual Branch Circuit A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

Think about a 60 amp range receptacle on a 40 or 50 amp circuit.

Roger
 
I'm confused here, Table 210.21(B)(3) lists Circuit ratings in Amperes. For a 15A Circuit it says "Not over 15" refering to Receptacle Rating. Am I missing something or misunderstanding it?


Tom
 
Davis9 said:
I'm confused here, Table 210.21(B)(3) lists Circuit ratings in Amperes. For a 15A Circuit it says "Not over 15" referring to Receptacle Rating. Am I missing something or misunderstanding it?


Tom

And this is where the question was not specific enough if more than one receptacle was to be on this circuit, 210.21(B)(3) is for a branch circuit supplying two or more receptacles or outlets, I am assuming there was no other receptacles since there was no more information given.

Roger
 
Last edited:
That is a Individual Branch Circuit I.E. Homerun no other outlets. No?So if I install a 15A Homerun(Individual Branch Circuit), I can install a 20A Receptacle outlet potentially overloading the circuit? I can understand the 40A or 50A rules for ranges due to demand. But say a 20A pump with a standard 20A cord end, this could be plugged into a circuit only designed to handle a 15A corded pump. I can see the wording of 210.21(B)(1) though and I can see this. I'm not sure the OP was using an Individual Branch Circuit in his example, He may have though.

Tom:-?
 
Tom, it would not be anything but an inconvenience (and bad design) if the OCPD was tripping due to this installation.

Roger
 
boboelectric said:
In a nutshell,Do what you want to do, Just don't get it inspected, It won't pass.

Bob O.84,Pa.15330

Bob, give us an article that would prohibit it.

Roger
 