Outpatient ambulatory
hhsting
Glen bunie, md, us
Junior plan reviewer
I have outpatient ambulatory that has generator as backup. Their is one 200A ATS that feeds Panel M and S. Panel M has one circuit that feeds life and safety. Rest of the circuits in Panel M are critical or equipment branch. Panel S has all critical branch circuits.
Would NEC 2017 Article 700.3(F) Temporary Source of Power for Maintenance or Repair of the Alternate Source of Power apply here it only has one ATS that is mixed with life safety, critical and equipment branch? Its not life safety alone
You appear to be in MD. If so, you're on the 2023 NEC which changes things a lot on this. Specifically the 2017 rule where 517 allows article 700. It's very limited after 2017. 2020 NEC and current specifically state which sections of 700 that can be used. So first question is: Are you on the 2017 or later NEC editions as that's super important to understand for life safety or critical branch circuits. Regardless, the answer you're wanting isn't what you'll get most likely. Redundency is an option for specific things, but that redundency comes at a cost. More info is necessary to know for sure.
In NEC 2017
My question is Not about if certain items are allowed to be in life safety circuit or not.
See post #1 about my question