adunbar
Member
- Location
- lowell, ma
We have a 100KW, 480V, PV inverter that we need to load side tap to an existing 208V, 3 phase switchboard. We specced a 480V wye: 208V delta transformer to be wired between the inverter and the 3 pole breaker used as our PV tap point in the existing swithcboard. The electrician ordered a 480V Delta:208 Wye transformer.
Can we use the ordered transformer? The inverter does not require a neutral connection and the inverter manufacturer says the delta configured transformer is acceptable to them.
We are not sure if we will have voltage imbalances with this configuration. Also we're not sure of how to handle the GEC connections.
Can we use the ordered transformer? The inverter does not require a neutral connection and the inverter manufacturer says the delta configured transformer is acceptable to them.
We are not sure if we will have voltage imbalances with this configuration. Also we're not sure of how to handle the GEC connections.