Output VFD Cables in a Single Conduit

emartinez

New User
Location
Dallas, TX
Occupation
Project Engineer
Due to project constraints, I am proposing to use a single existing conduit to run 4 separate VFD shielded cables to 4 separate motors ~450 ft. Is this possible? I understand it’s not advisable, but I just wanted to run it by here first for other input.

We are planning on using the X-Olene - Okoseal Shielded VFD cables.
 
As you mentioned it's not advisable but the sheilding on the cable is really important to minimize the "cross talk". That cable you're planning on using has a 5 mil copper tape shield which is standard. But it has an overlap of only 25%, meaning half of that shield will be 10 mils thick but the other half will only be 5 mils thick. It would be better to find one with a 50% overlap wherein the shield will be 10 mils thick the entire lenght. A lot will depend on the voltage and voltage spikes the motors will generate. Even better would be to use a CCW VFD cable and forego the conduit alltogether and properly space each one.
 