Outside condenser and outside sprinkler pump circuits

Status
Not open for further replies.

Bassplaya

Member
Location
Cocoa
Occupation
Electrician
Does the 2p 30 amp circuit for the outside condenser have to be a dual function afci/gfci circuit breaker per 2021 code?
Does a 2p 20 amp circuit for a outside sprinkler pump have to be a dual function afci/gfci circuit breaker per 2021 code?
Tia
 
Good find.
That would mean residential wells, be they lawn sprinklers or not, require GFCI protection.
Is an outlet for a sprinkler or water pump utilization equipment?
You could say it is electromechanical. Is there an exception for utilization equipment?
 
Just curious, why would the 2020 NEC be a concern, Fl is under the 2017

Roger
 