Your questions seem to be loaded...
I don't believe a yes, yes answer is possible...???![]()
1) In you State, city, county, are you required to have a service disconnect outside?
2) Can you run unfused service conductors inside a house?
No1) In you State, city, county, are you required to have a service disconnect outside?
Yes, for a short distance2) Can you run unfused service conductors inside a house?
Just curious.
1) In you State, city, county, are you required to have a service disconnect outside?
2) Can you run unfused service conductors inside a house?
AZ = yes, no
as far as practable.Not in MA, RI or CT
not in NH
Yes, about 5' more or less.
Sure it is. Even if the local codes require the service disconnect to be located outside, that doesn't mean that that disconnect has to be fused. I can have an unfused disconnect outside, and run to a main swichboard inside, and have a main breaker on the switchboard.I don't believe a yes, yes answer is possible...???![]()
i think his "maybe" is based on job conditions.Huh? :-?
Sure it is. Even if the local codes require the service disconnect to be located outside, that doesn't mean that that disconnect has to be fused. I can have an unfused disconnect outside, and run to a main swichboard inside, and have a main breaker on the switchboard.
I was going to ask you for a code citation, but I found it: 230.91. I concede the point.. . . a service disconnect must have integral or adjacent overcurrent protection. I don't believe outside disconnect, inside ocp meets that requirement.
In WisconsinJust curious.
1) In you State, city, county, are you required to have a service disconnect outside?
2) Can you run unfused service conductors inside a house?