In my eyes, a service change or a new house with a service is one and the same. Unless the code calls out an exemption on existing services, which it doesn't, then you need to install an exterior disconnect.I'm in CT and was trying to determine if an outside disconnect for emergency use is required for a residential service change, or only for new houses. The code class I just took, the instructor was unsure
230.85(C) Replacement.
Where service equipment is replaced, all of the requirements of this section shall apply.
Exception:
Where only meter sockets, service entrance conductors, or related raceways and fittings are replaced, the requirements of this section shall not apply.
So just a meter socket swap wouldn't require a disconnect?Here you go...the nec 2020
That's the way I read it, You'll want to check with the AHJ. Nothing worst then a suprise.So just a meter socket swap wouldn't require a disconnect?
@Steve16 so existing house service upgrade requires installation of a CO now? Were surge protectors amended out too? Do you have to throw arc faults in the whole panel? Sorry, new to the game and this code is tough to interpret.